Electrical advice please

Archived from the Tools In Action forum (Around The House). This thread is read-only.

FoneguyMember since Mar 2016

 

**Disclaimer***

i am seeking advice, all safety procedures will be followed, along with an abundance of common sense …….

I am only doing the conduits and running wire now, not any hookups.

 

I will be installing an RV outlet on the side of my house. Conduit is sealed 1″ PVC. Length from panel to outlet is approx 25′.  Needs are a 50amp RV outlet, along with a 20amp GFI outlet. I will most likely use an RV style service panel that has both outlets and breakers, similar to those in a campground. I will run a conduit out of panel and buried for any future needs.

?? What size wire is needed. I am thinking #4..  with a 70amp breaker

 

THANKS Crew !!!!!!!

RickyMcGrathMember since Oct 2014

[External image (uploads.tapatalk-cdn.com), not copied]

4AWG based on the info you provided.

RickyMcGrathMember since Oct 2014

Foneguy wrote:

Thanks Ricky !!!

what app is that, please ?

DeWalt Mobile Pro.

RickyMcGrathMember since Oct 2014

It has 145 different calculators pertinent to construction. It’s pretty handy.

FoneguyMember since Mar 2016

RickyMcGrath wrote:

4 minutes ago, RickyMcGrath said:

It has 145 different calculators pertinent to construction. It’s pretty handy.

HAH !!!! Now I feel like a dumb ass !!!

i have that app…….

thanks for the help

FoneguyMember since Mar 2016

Looks like you added the electricians calculator pack  ?

i will use this more often now …..

JimboS1iceMember since Sep 2015

RickyMcGrath wrote:

It has 145 different calculators pertinent to construction. It’s pretty handy.

I love that app

RickyMcGrathMember since Oct 2014

Foneguy wrote:

Looks like you added the electricians calculator pack  ?

i will use this more often now …..

I added the full master pack with all calculators.

BMack37Member since Sep 2015

That is F-ing awesome! DL the app now, thanks

JimboS1iceMember since Sep 2015

BMack37 wrote:

That is F-ing awesome! DL the app now, thanks

You will have to pay for different calculations, best bet buy them all!

RickyMcGrathMember since Oct 2014

[External image (uploads.tapatalk-cdn.com), not copied]

[External image (uploads.tapatalk-cdn.com), not copied]

[External image (uploads.tapatalk-cdn.com), not copied]

noopsMember since Mar 2016

You may be better off running 3/2 Al. 70A is a weird size and #4 copper isn’t a common commodity. With 3/2 Al you can get NMD and strip off the jacket or run 3/2 ACWU. In any case a 1″ conduit may be an unpleasant pull as I’m guessing you have 2 90s? A 20′ U? 4 is as big as you can go in 1″ pipe so if you could do 1.25″ it would go smoother.

Sent from my SM-G930W8 using Tapatalk

RickyMcGrathMember since Oct 2014

noops wrote:

You may be better off running 3/2 Al. 70A is a weird size and #4 copper isn’t a common commodity. With 3/2 Al you can get NMD and strip off the jacket or run 3/2 ACWU. In any case a 1″ conduit may be an unpleasant pull as I’m guessing you have 2 90s? A 20′ U? 4 is as big as you can go in 1″ pipe so if you could do 1.25″ it would go smoother.

Sent from my SM-G930W8 using Tapatalk

Most Lowes and HD carry 4AWG THHN by the foot. For a short run…..

FoneguyMember since Mar 2016

RickyMcGrath wrote:

9 hours ago, RickyMcGrath said:

Most Lowes and HD carry 4AWG THHN by the foot. For a short run…..

I did a little re-engineering in my head… My needs were a lot less than I planned for, so I picked up some #6 …

wire not pulled yet, but I a sure this is going to be fine …